Onan/Cummins generator surging
#1029277
05/30/11 03:03 AM
|
Joined: May 2006
Posts: 709
OP
Rock Warrior
|
I recently got a 7.5KW marine diesel Onan generator for free. He said it hasn't been run in a while and the voltage regulator was bad(wired for 220 but said it puts out 300v). Anyway brought it home, stuck the fuel lines in a gallon of diesel and it fired up fairly easy. I turned it on and off a a few times and it worked great. I then took the hoses out of the gas can and put the can away. I came back to it a few hours later and it took alot of cranking to start(figured it was because the fuel lines were empty). After it did start the governor hunts/surges. The engine will start to slow way down and the governor will slam on the throttle, then back off, then back one, instead of staying at a constant RPM. Any idea what might have happened? Why would it work fine one minute then after sitting for a couple hours suddenly develop this problem? ![[Linked Image]](http://i940.photobucket.com/albums/ad248/AsphaltCowboy90/IMG_1322.jpg) ![[Linked Image]](http://i940.photobucket.com/albums/ad248/AsphaltCowboy90/IMG_1323.jpg)
1989 Montero 4dr V6 3.0l
|
|
Re: Onan/Cummins generator surging
[Re: 89montero]
#1029278
05/30/11 03:58 AM
|
Joined: Feb 2005
Posts: 7,458
Trail Leader
|
Wants to be coddled. Perhaps there is air in the fuel system and the injector(s) need(s) to be bled?
|
|
Re: Onan/Cummins generator surging
[Re: rxinhed]
#1029279
05/30/11 03:35 PM
|
Joined: Jan 2001
Posts: 13,649
Web Wheeler
|
It spilled it's seed upon the ground...
Why a company named Cummins would buy a company named Onan is just beyond me, unless, just perhaps, they have a sense of humor? Nah, not possible...
Not responsible for advice not taken...
|
|
Re: Onan/Cummins generator surging
[Re: rxinhed]
#1029280
05/30/11 03:55 PM
|
Joined: Aug 2000
Posts: 4,868
Roll Me Over
|
Wants to be coddled. Perhaps there is air in the fuel system and the injector(s) need(s) to be bled? Onans have been the standard for marine generators for many years. I agree that it sounds as though the injectors need bleeding. With the older marine diesels, you have to be absolutely religious about not getting air into the lines. They are not self bleeding. I would see if you can find a users manual on-line that will detail the bleeding procedure for that particular model of engine.
|
|
Re: Onan/Cummins generator surging
[Re: 89montero]
#1029281
05/30/11 06:27 PM
|
Joined: Sep 2009
Posts: 235
Wheeler
|
That's how they run (the older ones) with out a load. Run an electric tool on it and it should run normal.
I worked on those/ sold those for years. They are a bit grumpy, but they are strong...
"Does this part need to be in there?"
1996 Dodge 1500 single cab / short bed, 5.9 4x4; 2" lift (springs not blocks), C.A.I and more mods to come.
|
|
Re: Onan/Cummins generator surging
[Re: DRX350]
#1029282
05/30/11 07:53 PM
|
Joined: Feb 2005
Posts: 2,649
Roll Me Over
|
Your Gen set looks like mine.
Do a search for 7.5 MDJE, there is tons of information out there including manuals,
Like mention above you need at least a 100 watt light bulb for it to generate a voltage.
Michael j
TreadLightly! Trainer
Grasscat III, 1994 Gen 2 Five speed, Stock ( for a little while )
GrassCat II, 1998 Gen 2.5 Locked and loaded. Ran off with Hector.
GrassCat I, 1991 Gen 1 Ran off with Justice.
|
|
Re: Onan/Cummins generator surging
[Re: Grasscat]
#1029283
05/30/11 07:55 PM
|
Joined: May 2006
Posts: 709
OP
Rock Warrior
|
thanks, I was thinking it had something to do w air in the fuel lines, it started right after I let the lines drain back. I will try to find the manual to figure out how to bleed them.
1989 Montero 4dr V6 3.0l
|
|
Re: Onan/Cummins generator surging
[Re: 89montero]
#1029284
05/30/11 08:05 PM
|
Joined: Feb 2005
Posts: 2,649
Roll Me Over
|
Last edited by Grasscat; 05/30/11 08:10 PM.
Michael j
TreadLightly! Trainer
Grasscat III, 1994 Gen 2 Five speed, Stock ( for a little while )
GrassCat II, 1998 Gen 2.5 Locked and loaded. Ran off with Hector.
GrassCat I, 1991 Gen 1 Ran off with Justice.
|
|
Re: Onan/Cummins generator surging
[Re: Grasscat]
#1029285
06/01/11 09:16 AM
|
Joined: May 2006
Posts: 709
OP
Rock Warrior
|
Your Gen set looks like mine.
Do a search for 7.5 MDJE, there is tons of information out there including manuals, What does your outlet box look like? The PO had it hardwired into his house. Right now when I take the cover off the box there are 4 identical wires(ignore the PO's splicing). Was there a electrical plug in stock? Cover on: ![[Linked Image]](http://i940.photobucket.com/albums/ad248/AsphaltCowboy90/IMG_1323.jpg) Cover off: ![[Linked Image]](http://i940.photobucket.com/albums/ad248/AsphaltCowboy90/IMG_1325.jpg)
1989 Montero 4dr V6 3.0l
|
|
Re: Onan/Cummins generator surging
[Re: 89montero]
#1029286
06/01/11 05:57 PM
|
Joined: Feb 2005
Posts: 2,649
Roll Me Over
|
Sorry Colin,but my Gen set is at the boat yard. There was no AC plug on the unit, just hard wired.
If your unit is a 3CR (like 7.5 MDJE 3CR) than here's how to hook it up.
For 1 phase, 2wire, 120 volts T1 & T3 are tied together. (Hot) T2 & T4 are tied together. (Ground)
For 1 phase, 3 wire, 120/240 volts T1 (Hot) T2 & T3 are tied together. (Ground) T4 (Hot)
For 1 phase, 2 wire, 240 volts. T1 & T4 are tied together. T2 (Ground) T3 (Hot)
Note: T2 must be grounded. Any other ground will cause serious damage to exciter.
It's been many years since I wired mine and I don't remember if the wires where marks or not. Maybe Bob can provided some more information.
Michael j
TreadLightly! Trainer
Grasscat III, 1994 Gen 2 Five speed, Stock ( for a little while )
GrassCat II, 1998 Gen 2.5 Locked and loaded. Ran off with Hector.
GrassCat I, 1991 Gen 1 Ran off with Justice.
|
|
|
|